设备调试过程中系统频繁死机,故障模块:6ES7 331-7KF02-0AB0,故障通道是6-7通道,输入值为2个压力值,开始采用2线制,系统报故障,然后系统采用4线制,系统可以正常工作,但是就是运行过程中频繁导致PLC死机,需重启PLC,故障信息如下,请高手帮忙分析下,接线没有错误
Diagnostic buffer of module CPU 315-2 DP
Order No./ Description Component Version
6ES7 315-2AG10-0AB0 Hardware 7
- - - Firmware V 2.6.4
Boot Loader Firmware expansion A 0.21.0
Rack: 0
Slot: 2
Event 1 of 10: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
08:25:23.990 AM 01/10/2010
Event 2 of 10: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by STOP command
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:25:23.987 AM 01/10/2010
Event 3 of 10: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by STOP command
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:25:23.111 AM 01/10/2010
Event 4 of 10: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
08:25:22.745 AM 01/10/2010
Event 5 of 10: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 1
Incoming event
08:25:21.256 AM 01/10/2010
Event 6 of 10: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:25:16.369 AM 01/10/2010
Event 7 of 10: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
08:25:00.847 AM 01/10/2010
Event 8 of 10: Event ID 16# 457F
STOP caused by STOP command
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FB number: 49
Module address: 3526
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incom
Event 9 of 10: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Analog SM
Input address: 256
Channel information available
Module/submodule fault
External module error
Channel error detected
Requested OB: Diagnostic interrupt OB (OB82)
Priority class: 26
External error, Incoming event
08:24:20.748 AM 01/10/2010