315-2DP BF灯亮报警 点击:2933 | 回复:13



LN368

    
  • 精华:0帖
  • 求助:40帖
  • 帖子:306帖 | 1715回
  • 年度积分:0
  • 历史总积分:6747
  • 注册:2004年9月09日
发表于:2013-06-27 12:03:55
楼主

315-2DP带得有几个模块,现在BF报警,可以运行,有几台都这样,有个别的过段时间又不报警了。信息如下。这是什么问提?

Diagnostic buffer of module CPU 315-2 DP

Order No./ Description         Component                      Version                       
6ES7 315-2AG10-0AB0            Hardware                       3                             
- - -                          Firmware                       V 2.0.8                       

Rack:                          0
Slot:                          2
Event 1 of 10:  Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information: 
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types: 
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
05:06:56.465 PM  06/24/2013


Event 2 of 10:  Event ID 16# 1382
Request for automatic warm restart 
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types: 
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
05:06:56.463 PM  06/24/2013


Event 3 of 10:  Event ID 16# 4301
Mode transition from STOP to STARTUP 
STOP due to: Power failure
Startup information: 
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types: 
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
05:06:56.016 PM  06/24/2013


Event 4 of 10:  Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master 
Slot of the DP master:   2 
Number of distributed stations:   0
Incoming event
05:06:44.604 PM  06/24/2013


Event 5 of 10:  Event ID 16# 4300
Power on backed up 
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
05:06:41.506 PM  06/24/2013


Event 6 of 10:  Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
05:06:22.920 PM  06/24/2013


Event 7 of 10:  Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information: 
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types: 
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
04:59:11.221 PM  06/24/2013


Event 8 of 10:  Event ID 16# 1382
Request for automatic warm restart 
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types: 
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
04:59:11.219 PM  06/24/2013


Event 9 of 10:  Event ID 16# 4301
Mode transition from STOP to STARTUP 
STOP due to: Power failure
Startup information: 
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types: 
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
04:59:10.742 PM  06/24/2013


Event 10 of 10:  Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master 
Slot of the DP master:   2 
Number of distributed stations:   0
Incoming event
04:58:59.373 PM  06/24/2013


 

 




研讨会宣传员_3259

  • [版主]
  • 精华:3帖
  • 求助:110帖
  • 帖子:1927帖 | 14403回
  • 年度积分:102
  • 历史总积分:64749
  • 注册:2020年3月27日
发表于:2013-06-27 12:18:35
1楼

看不懂洋文,,郁闷。。。。。          

研讨会宣传员_3259

  • [版主]
  • 精华:3帖
  • 求助:110帖
  • 帖子:1927帖 | 14403回
  • 年度积分:102
  • 历史总积分:64749
  • 注册:2020年3月27日
发表于:2013-06-27 12:20:22
2楼

翻译一下:

10事件1:事件ID 16#4302
从启动到运行模式转换
启动信息:
- 时间时间戳上次备份电源
- 单处理器操作
当前/上次启动类型:
- 通过开关设置触发暖重启;最后电源备份
允许一定的启动类型:
- 允许手动暖重启
- 允许自动暖重启
最后一个有效操作或设置电源自动启动类型:
- 通过开关设置触发暖重启;最后电源备份
以前的操作模式:启动(热启动)
请求的操作模式:RUN
进入事件
2013年6月24日下午05:06:56.465


事件2:事件ID 16#1382
请求自动暖重启
STOP由于:电源故障
启动信息:
- 启动无需修改系统配置
- 设定值和实际配置没有区别
- 时间时间戳上次备份电源
- 单处理器操作
当前/上次启动类型:
- 通过开关设置触发暖重启;最后电源备份
允许一定的启动类型:
- 允许手动暖重启
- 允许自动暖重启
最后一个有效操作或设置自动启动电源类型:
- 通过开关设置触发暖重启;最后电源备份
要求OB:启动OB(OB100)
优先级:27
进入事件
2013年6月24日下午05:06:56.463


3 10事件:事件ID 16#4301
从STOP模式转换启动
STOP由于:电源故障
启动信息:
- 时间时间戳上次备份电源
- 单处理器操作
当前/上次启动类型:
- 通过开关设置触发暖重启;最后电源备份
允许一定的启动类型:
- 允许手动暖重启
- 允许自动暖重启
最后一个有效操作或设置自动启动电源类型:
- 通过开关设置触发暖重启;最后电源备份
以前的操作模式:STOP(内部)
请求的操作模式:启动(热启动)
进入事件
2013年6月24日下午05:06:56.016


10事件4:事件ID 16#5371
分布式I / O:DP主站同步结束
DP主站的插槽:2
分布式站数:0
进入事件
2013年6月24日下午05:06:44.604


10事件5:事件ID 16#4300
电源备份
以前的操作模式:无电压
请求的操作模式:STOP(自己的初始化)
进入事件
2013年6月24日下午05:06:41.506


10事件6:事件ID 16#494E
停电
以前的操作模式:RUN
请求的操作模式:无电压
外部错误,进入事件
2013年6月24日下午05:06:22.920


7 10事件:事件ID 16#4302
从启动到运行模式转换
启动信息:
- 时间时间戳上次备份电源
- 单处理器操作
当前/上次启动类型:
- 通过开关设置触发暖重启;最后电源备份
允许一定的启动类型:
- 允许手动暖重启
- 允许自动暖重启
最后一个有效操作或设置电源自动启动类型:
- 通过开关设置触发暖重启;最后电源备份
以前的操作模式:启动(热启动)
请求的操作模式:RUN
进入事件
2013年6月24日下午04:59:11.221


8 10事件:事件ID 16#1382
请求自动暖重启
STOP由于:电源故障
启动信息:
- 启动无需修改系统配置
- 设定值和实际配置没有区别
- 时间时间戳上次备份电源
- 单处理器操作
当前/上次启动类型:
- 通过开关设置触发暖重启;最后电源备份
允许一定的启动类型:
- 允许手动暖重启
- 允许自动暖重启
最后一个有效操作或设置自动启动电源类型:
- 通过开关设置触发暖重启;最后电源备份
要求OB:启动OB(OB100)
优先级:27
进入事件
2013年6月24日下午04:59:11.219


9 10事件:事件ID 16#4301
从STOP模式转换启动
STOP由于:电源故障
启动信息:
- 时间时间戳上次备份电源
- 单处理器操作
当前/上次启动类型:
- 通过开关设置触发暖重启;最后电源备份
允许一定的启动类型:
- 允许手动暖重启
- 允许自动暖重启
最后一个有效操作或设置自动启动电源类型:
- 通过开关设置触发暖重启;最后电源备份
以前的操作模式:STOP(内部)
请求的操作模式:启动(热启动)
进入事件
2013年6月24日下午04:59:10.742


10事件10:事件ID 16#5371
分布式I / O:DP主站同步结束
DP主站的插槽:2
分布式站数:0
进入事件
2013年6月24日下午04:58:59.373

银光人生—华

  • 精华:0帖
  • 求助:0帖
  • 帖子:5帖 | 13597回
  • 年度积分:0
  • 历史总积分:52877
  • 注册:2007年11月23日
发表于:2013-06-27 12:52:30
3楼

子站是DP方式通信吗?

只要有一个站没通信上的话就会报错误的;但是不影响PLC运行的;

阿水--王者之师

  • 精华:24帖
  • 求助:348帖
  • 帖子:1616帖 | 22281回
  • 年度积分:37
  • 历史总积分:98482
  • 注册:2007年3月22日
发表于:2013-06-27 13:04:03
4楼

  2 楼的强大呀 !


从站通讯出了故障 !还有电源故障

狼牙精神

  • 精华:6帖
  • 求助:5帖
  • 帖子:468帖 | 5379回
  • 年度积分:119
  • 历史总积分:62906
  • 注册:2020年3月27日
发表于:2013-06-27 13:04:52
5楼

1-3、7-9号事件是因为电源故障后进入STOP模式,电源恢复后的自动暖启动过程。

4、10号事件DP通讯问题,检查一下通讯线路。

6号事件是电源故障,从STOP模式切换到无电压模式。

5号事件是从无电压模式切换到STOP模式(自己初始化),电源自动恢复了。

对于电源故障检查一下各站电源接线是否有松动。

由于程序里边有OB82和OB86出现短暂电源故障又恢复后,CPU会调用OB82和OB86自动启动。

 

 

从未被超越

  • 精华:3帖
  • 求助:11帖
  • 帖子:108帖 | 1584回
  • 年度积分:1
  • 历史总积分:12293
  • 注册:2011年12月09日
发表于:2013-06-27 13:11:13
6楼

BF报警可能是静电接地的原因,主要是检查你卡件接的点都是什么点,比如说AI点事变送器还是热偶呀,如果两者混要接就会出现BF报警。

liuyy601888

  • 精华:0帖
  • 求助:1帖
  • 帖子:2帖 | 40回
  • 年度积分:0
  • 历史总积分:71
  • 注册:2013年6月28日
发表于:2013-06-28 10:48:17
7楼

可是你不懂,拿分走人

liuyy601888

  • 精华:0帖
  • 求助:1帖
  • 帖子:2帖 | 40回
  • 年度积分:0
  • 历史总积分:71
  • 注册:2013年6月28日
发表于:2013-06-28 10:48:41
8楼

打错了 是我不懂  拿分走人

liujian1826

  • 精华:0帖
  • 求助:19帖
  • 帖子:20帖 | 54回
  • 年度积分:0
  • 历史总积分:196
  • 注册:2011年3月14日
发表于:2013-07-03 00:08:44
9楼

BF 外部通讯故障,DP网络至少有一个节点没有通讯。

边城子夜

  • 精华:0帖
  • 求助:3帖
  • 帖子:17帖 | 160回
  • 年度积分:0
  • 历史总积分:216
  • 注册:2008年12月13日
发表于:2013-07-04 14:04:20
10楼

楼上正解!如果有DP/DP耦合器,先把它拿掉试试

 

  • 精华:0帖
  • 求助:5帖
  • 帖子:34帖 | 290回
  • 年度积分:0
  • 历史总积分:579
  • 注册:2007年8月27日
发表于:2013-07-07 20:31:21
11楼

应该是DP某站有通信故障,但是不影响正常操作

lucifer33332

  • 精华:0帖
  • 求助:0帖
  • 帖子:0帖 | 55回
  • 年度积分:0
  • 历史总积分:20
  • 注册:2013年7月09日
发表于:2013-07-12 17:03:24
12楼

检查dp头吧,我经常遇到这情况

十年河西

  • 精华:0帖
  • 求助:0帖
  • 帖子:0帖 | 104回
  • 年度积分:0
  • 历史总积分:46
  • 注册:2013年9月10日
发表于:2013-09-11 03:11:54
13楼

如果调用了OB82,OB86,这是DP从站的,就是从站丢失,CPU也不会重启,调用了OB122,即使模块没有,CPU也不会重启,这是模块问题或者干扰问题。