to hh.carlo,
W#16#2942 I/O access error, reading OB 122
You must concentrate on two things, besides collecting the diagnostic messages from all affected modules, as suggested earlier: This, by the way, would be essential, especially on the AI modules.
You get the message "the configuration of the station in HW is defferent than the exist in the plant" when this requirement is marked with a check in the CPU propertiies (HWConfig). If this is checked, your DP master will only operate if there are no diagnostic messages from the configured slaves. Unchecking this requirement will allow the master to connect to slaves that do not give diagnostic messages.
Second: your ET 200M IMs are giving diagnostic errors because they cannot reach certain addresses (these you show in the diagnostic buffer messages). So: are these addresses the ones of the AI modules that also show fault signals? If they are: What is the diagnostic buffer contents for these modules (double-click on the AI modules marked with a red slash in the Online view of HWConfig). Please then start by fixing the problem on these modules, then see if this clears the faults on the ET 200M stations.