Problem: "Downloading" a ControlLogix project with one computer and attempting to "Upload" from another computer... the other computer may receive the following error message: "there was unspecified communications problem Rslogix5000 has been taken offine."
Cause: In this particular case, the problem was a result of an orphaned or invalid tag downloaded to the controller. The results reported Error: Name is invalid. Error: Failed to upload tags.
Workaround:
1.Save the program "as" .L5K format.
2.Then open the .L5K file back into RSLogix 5000 software to make a new .ACD file.
3.Download the newly constructed .ACD file and now it Uploads correctly.
4.Reschedule any ControlNet connections.
---------------------------------------------------------------------------------------------------------
ROCKWELL AUTOMATION (SHENZHEN) BRANCH
Customer Service & Maintenance Area Manager
Nemo Yu
Mobile:18820272797
Email:yfyu@ra.rockwell.com
您好,
以下是ROCKWELL AUTOMATION KNOWLEDGEBASE为您作出的解答:非常感谢。
Problem: "Downloading" a ControlLogix project with one computer and attempting to "Upload" from another computer... the other computer may receive the following error message: "there was unspecified communications problem Rslogix5000 has been taken offine."
Cause: In this particular case, the problem was a result of an orphaned or invalid tag downloaded to the controller. The results reported Error: Name is invalid. Error: Failed to upload tags.
Workaround:
1.Save the program "as" .L5K format.
2.Then open the .L5K file back into RSLogix 5000 software to make a new .ACD file.
3.Download the newly constructed .ACD file and now it Uploads correctly.
4.Reschedule any ControlNet connections.
---------------------------------------------------------------------------------------------------------
ROCKWELL AUTOMATION (SHENZHEN) BRANCH
Customer Service & Maintenance Area Manager
Nemo Yu
Mobile:18820272797
Email:yfyu@ra.rockwell.com