关于s7-400的CPU故障诊断 点击:718 | 回复:2



魑魅魍魉

    
  • 精华:0帖
  • 求助:0帖
  • 帖子:16帖 | 75回
  • 年度积分:0
  • 历史总积分:292
  • 注册:2005年10月25日
发表于:2008-05-24 15:08:40
楼主
请大家帮我诊断一下CPU停机的和原因 ,诊断如下:其中通信速率为500K,当速率提升到3M以上时大部分子站掉站情况!诊断时钟有问题(详见对中部分)
Event 1 of 120: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 90
DP master system ID: 1
Log. base address of the DP slave: Input address: 16358
Log. base address of the DP master: 16383
OB number: 86
Priority class: 26
External error, Outgoing event
01:54:43:223 am 05/22/08


Event 2 of 120: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 90
DP master system ID: 1
Log. base address of the DP slave: Input address: 16358
Log. base address of the DP master: 16383
OB number: 86
Priority class: 26
External error, Incoming event
01:54:43:151 am 05/22/08


Event 3 of 120: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 22
DP master system ID: 1
Log. base address of the DP slave: Input address: 16359
Log. base address of the DP master: 16383
OB number: 86
Priority class: 26
External error, Outgoing event
12:40:11:683 am 05/22/08


Event 4 of 120: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 584
FC number: 1240
Module address: 48
OB number: 122
Priority class: 1
External error, Incoming event
12:40:11:679 am 05/22/08


Event 5 of 120: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 584
FC number: 1240
Module address: 16
OB number: 122
Priority class: 1
External error, Incoming event
12:40:11:679 am 05/22/08


Event 6 of 120: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 584
FC number: 1240
Module address: 2
OB number: 122
Priority class: 1
External error, Incoming event
12:40:11:678 am 05/22/08


Event 7 of 120: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 584
FC number: 1240
Module address: 48
OB number: 122
Priority class: 1
External error, Incoming event
12:40:11:673 am 05/22/08


Event 8 of 120: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 584
FC number: 1240
Module address: 16
OB number: 122
Priority class: 1
External error, Incoming event
12:40:11:673 am 05/22/08


Event 9 of 120: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 584
FC number: 1240
Module address: 2
OB number: 122
Priority class: 1
External error, Incoming event
12:40:11:673 am 05/22/08


Event 10 of 120: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 584
FC number: 1240
Module address: 48
OB number: 122
Priority class: 1
External error, Incoming event
12:40:11:667 am 05/22/08


Event 11 of 120: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 584
FC number: 1240
Module address: 16
OB number: 122
Priority class: 1
External error, Incoming event
12:40:11:667 am 05/22/08


Event 12 of 120: Event ID 16# 2942


楼主最近还看过



千山独步

  • 精华:0帖
  • 求助:0帖
  • 帖子:159帖 | 3098回
  • 年度积分:4
  • 历史总积分:21261
  • 注册:2007年2月02日
发表于:2008-05-24 19:42:32
1楼
检查干扰源,降低波特率. 

happy123

  • 精华:0帖
  • 求助:0帖
  • 帖子:0帖 | 13回
  • 年度积分:0
  • 历史总积分:100
  • 注册:2008年5月04日
发表于:2008-06-01 00:52:17
2楼

刚看一下,有些明白,我估计是组态硬件时其中有些通信速率 有问题,具体要看组态你能否把程序发份给我,我们共同进步,共同提高,