Under normal conditions, the invert size dimensioning parameters have to be set only once, and this is done at the manufacturing pant prior to delivery. However, the parameter must be re-defined after a replacement RMIO-01/-02 board has been installed. The parameters are not intended to be changed by the user, and they are not deal with in the ACS 800 Firmware Manual in order to gain access to Parameter Group 112, code 564 must be entered at Parameter 16.3 (PASS CODE). (See the ACS 800 Firmware Manual for details on how to modify parameter values.) Do not alter any other parameter values. Altering the wrong parameters, or entering the wrong values for these parameter, voids the warranty, The value in the table must be rounded if necessary. IMPORTANT! When using parameter 112.06 for reconfigured a unit size to an other size. A board already configured for a unit size must always be reconfigured via the selection xxNONE. For example when transferring the RMIO-01 from an 0020-03 unit to an 0040-05 unit, the procedure is as follows: 1) Access parameter 99.03 and set the value YES (Factory settings become effective) 2) Access parameter 112.06 as described above. Set value to xxNONE. 3) Switch power off and then on again. 4) Access parameter 112.06. Set value sr0040_05. 5) Switch power off and then on again.
修改失败,请分析原因 1) Access parameter 99.03 and set the value YES (Factory settings become effective) 问题:改成yes有报警,并自动变成no 2) Access parameter 112.06 as described above. Set value to xxNONE 问题:没有找到参数112.06,从112.05直接到112.07了