S7-300系统经常出现停机报警,AI模块也坏了几块了(334),CPU的报警记录谁能帮忙解释一下,在此先谢谢了。

Event 1 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 105
Module address: 46
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
10:02:31:563 pm 09/18/10


Event 2 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 280
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
10:02:31:553 pm 09/18/10


Event 3 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
10:02:31:538 pm 09/18/10


Event 4 of 100: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
10:02:31:537 pm 09/18/10


Event 5 of 100: Event ID 16# 5961
Parameter assignment error in CPU module parameters
Parameter: module type
Output address: 44 of the module with parameter assignment errors
Error type: configurable slot empty
Operating mode: STARTUP (warm restart)
External error, Incoming event
10:02:31:302 pm 09/18/10




yidao

  • 精华:0帖
  • 求助:0帖
  • 帖子:1帖 | 2回
  • 年度积分:0
  • 历史总积分:16
  • 注册:2007年10月31日
发表于:2010-10-20 19:22:47
1楼

报警共有100条,不好意思全发,有热心的朋友可以发邮件(sxhcxzsqy@163.com)或QQ:375618449

在线等待!!!

彩云之滇东北

  • 精华:20帖
  • 求助:5帖
  • 帖子:107帖 | 2725回
  • 年度积分:0
  • 历史总积分:21121
  • 注册:2005年6月14日
发表于:2010-10-20 20:53:07
2楼
顶一下                                            

zwb625880

  • 精华:0帖
  • 求助:0帖
  • 帖子:5帖 | 22回
  • 年度积分:8
  • 历史总积分:306
  • 注册:2008年8月01日
发表于:2010-10-20 21:17:32
3楼

事件ID 16#4563
停止造成的I / O访问错误(OB没加载或无法实现)
在用户程序中断点:循环程序(OB1中)
优先级:1
功能号:105
模块地址:46
先前的运行模式:运行
请求的操作模式:停止(内部)
内部错误,输入事件
你的配置是否有问题?启动过程要求跳转到OB100

yidao

  • 精华:0帖
  • 求助:0帖
  • 帖子:1帖 | 2回
  • 年度积分:0
  • 历史总积分:16
  • 注册:2007年10月31日
发表于:2010-10-20 21:48:18
4楼

以前系统都一直运行较好,只是在9月15日打雷后就这样了,而且近期334模块(AI)接受的4-20mA的信号正常,但在操作员站上却都是满量程,求教西门子客服,要求将AI模块进线负端与模块20号端子(M端)连接,照做,故障依旧,停PLC系统电源,操作员站上还是显示满量程。

0953

  • 精华:1帖
  • 求助:0帖
  • 帖子:63帖 | 338回
  • 年度积分:0
  • 历史总积分:842
  • 注册:2004年8月05日
发表于:2010-10-21 08:24:54
5楼

FC number: 105

这是模拟量量程标定转换块。估计雷击造成AI通道损坏。